In climates with less than 4,000 Heating Degree Days, materials like painted gypsum wallboard and plaster wall coatings impede moisture diffusion to acceptable levels. Usually, no further vapor diffusion retarder is needed.
In more extreme climates, vapor diffusion retarders are advisable for new construction. They perform best when installed closest to the warm side of a structural assembly; in cold climates, this is towards the interior of the building. In hot/wet climates, this is towards the exterior of the building.
Reasonable rules-of-thumb to follow when placing vapor retarders include the following:
*
In climates with 2,200 or more Heating Degree Days, locate the vapor diffusion retarder on the warm side of the exterior structural assembly. If possible, locate it on the inside of the assembly using the "one-third, two-thirds rule": the vapor diffusion retarder has one-third of the cavity insulation to its warm side, two-thirds to the cold side. This protects the retarder from physical damage through errant construction or remodeling activities.
*
In climates with fewer than 2,200 Heating Degree Days (cooling-dominated climates) and where the building is near, but not quite in, the 2,200 Heating Degree Days zone (a.k.a. fringe zone), place the vapor diffusion retarder in the same location as climates farther north.
*
Farther south (about 1,900 Heating Degree Days) it is unimportant where the vapor diffusion retarder goes. For climates even farther south and generally hotter and more humid, some professionals recommend omitting the vapor diffusion retarder completely. This is due to the winter heating loads and summer cooling loads being roughly equal. Any location ends up having the vapor diffusion retarder on the wrong side of the structure during part of the year. However, other building science research indicates that it should be applied directly under the exterior finish and is sometimes itself the exterior finish. A combination air barrier/vapor diffusion retarder may be a better choice for this situation.
Knowledgeable builders typically use vapor diffusion retarders with ratings of 0.1 or less. However, if you carefully seal the warm-side vapor diffusion retarder and interior finish, you can also safely install a low-permeable material, such as rigid foam board insulation (a perm rating as high as 1.4), on the cold side of walls. A good rule-of-thumb: to prevent trapping any moisture in a cavity, the cold-side material's perm rating should be at least five times greater than the value of the warm-side. Use a vapor diffusion retarder with a perm value of less than 0.50 if you also have a high water table.